Will R407c Work In A R410a Condenser?

1 reading
26K views 17 replies 13 participants last post by  Special-K  
#1 ·
I have a customer whose side yard is very narrow at 5', not unusual here in Southern California, he had an R22 system installed at the tail end of the phase out of the "dry charge" R22 units so the system isn't in too bad of shape. The problem is the existing condenser blocks almost the entire access on the side yard. He'd like a side discharge "slim line" condenser to regain access to the side yard but there are none that I'm aware of that aren't R410a and the customer doesn't want to spend the money on a new R410a system.

I've done several R407c retrofits that have worked well and that got me questioning what would happen if you recovered all the R410a from a "slimline" condenser and charged it with R407c? I'm sure that would void any warranty but they both use POE, the compressors built for higher pressures so maybe that's a positive. I understand the R410a compressor has smaller capacity but would there be some type of offset that would let the system work?

Has anyone tried this combination successfully? Just kind of curious....

Kirk
 
#12 ·
410 conversion to 407. Why 35% Efficiency loss?



Will the 407 pump out at the higher pressure in a 410 condensing unit because of mechanical design, inability to remove heat.... or will the 407 control the pressure because of characteristics? Will the condenser coil not remove heat and liquify the 407. Need logical answers for my mind. If the evap coil works well with the 407, "why" will it loose 35% efficiency. Has anyone tried it? or is this pen and paper calculations?...terry
 
#9 ·
I know this is an old thread. The answers remind me of my wife. Never can answer a question. Don't need to help anyone, no advice needed, no reason to ask why I need the answer please. Can you put a dry r410 condensing unit on an existing r407 system, re-fill with r407? and would the efficiency drop excessively? Ty...terry
 
#10 ·
Can you relocate the condensing unit to the roof? I have come to prefer that for a number of good reasons.

You can use the R-407C in the R-410 system - IF it has a piston metering device.

If there is a TXV - that will have to be changed to R-407 as well.

When you are choosing the new TXV bear in mind that the system capacity will be 33% lower than it is with R-410.

If it is 3 tons now - it will be 2 tons after the refrigerant change. Piston or TXV - 1/3 less BTU capacity.

PHM
-------
 
Save
#11 ·
410 to 407 Conversion Question

I'm a new member. Can you put a dry r410 condensing unit on an existing r407 system, re-fill with r407? and would the efficiency drop excessively? Have an auction for cheap lennox 3.5T heat pump units, want to put on existing 407 systems without modifications. Can it be done without severely limiting efficiently. I own the properties. Not customers. Know there is no warranty. Is there an extreme physical difference in the two compressors?


I realize the operating pressures are radically different. Is this because of the refrigerant properties or the compressor and condensing unit? Would 407 work close to its normal pressures with a 410 condensing unit? Are the compressors radically different, or what is the reason for inability to remove and absorb the heat? I just need a reason as to why it is a bad idea as some say...terry
 
#13 ·
Will the 407 pump out at the higher pressure in a 410 condensing unit because of mechanical design, inability to remove heat.... or will the 407 control the pressure because of characteristics? Need logical answers for my mind. If the evap coil works well with the 407, "why" will it loose 35% efficiency. I'm putting in a 42000 btu condenser on a 36000 btu system. Has anyone tried it? or is this pen and paper calculations?...terry
 
#15 ·
I'm putting in a 42000 btu condenser on a 36000 btu system. Has anyone tried it? or is this pen and paper calculations?...terry
It has been done by several people on here and works well.
Poodle Head Mikey was the first.
Sent from the Okie state usin Tapatalk
"Is this before or after you fired the parts cannon at it?" - senior tech
 
Save
#16 ·
To understand correctly, the 410 condenser unit will have 35% more efficiency when using 407 in removing the heat than the existing 407 condenser. Is this correct? The 407 will liquify and go to evap at a lower pressure. I'm putting a 42K btu 410 condenser on a 36K btu system to increase fluid capacity. Same oil. What will happen?
 