I can understand why the liquid line is cold or frozen when the refrigerant is low, but can't understand why the suction line is hot.
can someone please explain?
can someone please explain?
The warmest a suction line can be is whatever the return air temperature that is blowing across the evaporator is. I don't think it can physically be any warmer than that (unless we're talking about a heat pump when the suction line turns into the discharge line).
Also, the liquid line wouldn't ever be cold or frozen, unless the filter drier is plugged up, which is kind of a rare phenomenon. Are you sure you don't have what you think are the liquid and suction lines mixed up?
If a system is low of refrigerant then you would have zero subcooling, which would tend to make the liquid line WARMER than normal. At the same time the lower low side pressure would make the temperature of the refrigerant in the beginning part of the evaporator colder than normal, which could cause it to freeze up starting near the expansion valve and eventually the entire coil and suction line back to the compressor.
Are you just messing with us?
That’s not what happens at all.I think I can answer my own question now, correct me if I am wrong.
When the freon is low, initially, as ammoniadog said, the suction line (low side) will the frozen, and the liquid line (high side) will be warm. But if you keep the system on, then the frozen will go through the compressor and all the way through the liquid line back to the expansion valve (where the frozen started initially), i.e., the entire system is frozen up. AND THEN, because there is no freon getting into the suction line, the compressor is essentially making a vacuum on the suction line, which will make a hot. That's why when the system is low on freon and you keep the system running, eventually the liquid line will be frozen and the suction line will be warm.
It can get pretty warm if the captube is soldered to it for heat transfer.The warmest a suction line can be is whatever the return air temperature that is blowing across the evaporator is. I don't think it can physically be any warmer than that (unless we're talking about a heat pump when the suction line turns into the discharge line).
Also, the liquid line wouldn't ever be cold or frozen, unless the filter drier is plugged up, which is kind of a rare phenomenon. Are you sure you don't have what you think are the liquid and suction lines mixed up?
If a system is low of refrigerant then you would have zero subcooling, which would tend to make the liquid line WARMER than normal. At the same time the lower low side pressure would make the temperature of the refrigerant in the beginning part of the evaporator colder than normal, which could cause it to freeze up starting near the expansion valve and eventually the entire coil and suction line back to the compressor.