A fair amount has been written aout this, and I've seen conflicing views.
First I know most all tech have hoses that technically are charging hoses, not vacuum hoses. There's talk of hose pressure migration, apparently another name for vacuum loss through the hose wall. I've also seen my sman leak through the high side valve. (now fixed)
There's talk of suspected water trapped under compressor oil. Not sure if a deep vac removes any of that or not, and maybe we'll never know.
Some guys may triple vac with a nitro purge in between, waiting __ min to allow nitro to absorb moisture. Depending on the micron target, seems that could add an hour or two to a job.
Some vac once and done. Some may vac to 300 or 500, or even 1000, and don't wait for a rise.
Some pump mfgs say pump to 300, wait 20 min, and if you're still under 500, good to go. Some say ok if under 1000.
Perhaps its my new Robinair hoses, but every job yeilds a different rise in microns. Sometimes 500, sometimes 700, occasionally 1500. Sometimes it stops rising, but sometimes theres still a very slow rise after 20 min. How would you know if that's water, a leak, or hoses migrating pressure?
Interested to see what others do to satisfy themselves they have a good dry, tight system.
First I know most all tech have hoses that technically are charging hoses, not vacuum hoses. There's talk of hose pressure migration, apparently another name for vacuum loss through the hose wall. I've also seen my sman leak through the high side valve. (now fixed)
There's talk of suspected water trapped under compressor oil. Not sure if a deep vac removes any of that or not, and maybe we'll never know.
Some guys may triple vac with a nitro purge in between, waiting __ min to allow nitro to absorb moisture. Depending on the micron target, seems that could add an hour or two to a job.
Some vac once and done. Some may vac to 300 or 500, or even 1000, and don't wait for a rise.
Some pump mfgs say pump to 300, wait 20 min, and if you're still under 500, good to go. Some say ok if under 1000.
Perhaps its my new Robinair hoses, but every job yeilds a different rise in microns. Sometimes 500, sometimes 700, occasionally 1500. Sometimes it stops rising, but sometimes theres still a very slow rise after 20 min. How would you know if that's water, a leak, or hoses migrating pressure?
Interested to see what others do to satisfy themselves they have a good dry, tight system.