We got a new heat pump a couple of years ago, and ever since we go it it has been doing this. What happens is that if the coil temperature is just above freezing (so it doesn't auto defrost), and then the ambient temperature warms up, the frost at the top of the coil never clears.
Today, for example, OAT was around 32F this morning (so no auto defrost), and then it warmed up but there is still frost on the top quarter of the coil, and on various pipes:
OAT sensor=50F (has been this temp for 3+ hours)
coil sensor=50F
indoor temp=71F
heat register temp=86F
Then, I decided to manually defrost for 5 mins which completely removed the frost from the fins, coils and pipes. Afterwards:
OAT sensor=50F
coil sensor=48F
indoor temp=71F
heat register temp=93F
I'm just unsure if this is normal, as it seems a bit odd that the top of the coil should be frosted up at 50F (so presumably the top of the coil is <32F), yet the coil sensor is showing 50F. Is there that big a temperature difference over the coil? I wouldn't have thought so, as none of the coil is normally frosted up at this temp.
The problem is that when the temp stays just above 32F the top half of the coil remains frosted up and reduces the efficiency by 50%, even after the temperature warms up. When it warms up the coil partially defrosts, but the top quarter always remains frosted up unless you manually defrost, or the heat is off for a few hours.
Installer has serviced it about 4 times since, and each time temps and pressures are 100% perfect (but it's never been frosted up). They say that this model (GSZC160241CA) has a big coil and can handle a bit of frost. That is true, but the issue is that I have to manually defrost when it's been cold in the morning otherwise it takes twice as long to heat the house up, and I'm wondering if there is some issue with it or if this is normal.
This model has a duct around the fan to supposedly increase efficiency, but I'm wondering if the fan duct reduces airflow to the top quarter of the coil and that's what is causing the problem.
Auto defrost is working 100% perfectly. The problem is only when the coil temperature is just above 32F and then warms up. It would be nice if I was able to adjust the defrost temp via comfortnet, but they don't have that feature.
Today, for example, OAT was around 32F this morning (so no auto defrost), and then it warmed up but there is still frost on the top quarter of the coil, and on various pipes:
OAT sensor=50F (has been this temp for 3+ hours)
coil sensor=50F
indoor temp=71F
heat register temp=86F
Then, I decided to manually defrost for 5 mins which completely removed the frost from the fins, coils and pipes. Afterwards:
OAT sensor=50F
coil sensor=48F
indoor temp=71F
heat register temp=93F
I'm just unsure if this is normal, as it seems a bit odd that the top of the coil should be frosted up at 50F (so presumably the top of the coil is <32F), yet the coil sensor is showing 50F. Is there that big a temperature difference over the coil? I wouldn't have thought so, as none of the coil is normally frosted up at this temp.
The problem is that when the temp stays just above 32F the top half of the coil remains frosted up and reduces the efficiency by 50%, even after the temperature warms up. When it warms up the coil partially defrosts, but the top quarter always remains frosted up unless you manually defrost, or the heat is off for a few hours.
Installer has serviced it about 4 times since, and each time temps and pressures are 100% perfect (but it's never been frosted up). They say that this model (GSZC160241CA) has a big coil and can handle a bit of frost. That is true, but the issue is that I have to manually defrost when it's been cold in the morning otherwise it takes twice as long to heat the house up, and I'm wondering if there is some issue with it or if this is normal.
This model has a duct around the fan to supposedly increase efficiency, but I'm wondering if the fan duct reduces airflow to the top quarter of the coil and that's what is causing the problem.
Auto defrost is working 100% perfectly. The problem is only when the coil temperature is just above 32F and then warms up. It would be nice if I was able to adjust the defrost temp via comfortnet, but they don't have that feature.