Testing hot surface igniter
1 reading
12K views 14 replies 7 participants last post by  wfdtruck3
#1 ·
Other than the obvious cracked igniter, how can you test an HSI? I came across one that is getting 24V out of the gas valve to it but does not heat up at all.
#9 ·
I replaced the igniter because there is no glowing of the HSI. I fired it and it lit off as normal, once. After that it started the same thing.
#10 ·
When you say energize are you referring to the click just prior to the the HSI glowing? It does not make that click. But if I take a voltage reading I do get 24 volts
#12 ·
With all the different ignitors out there, ohm readings will vary from manufacturer to manufacturer... Some are good with ohms between 15-100, some are still good with ohms into the 400's...(Norton low-temps...)
#13 ·
Seems the hot surface ignitors I run across are 115 vac. I just plug them into a wall socket to see if they work. I always check the voltage to the ignitor first just to be sure.
Save
#15 ·
Come to find out it was a bad gas valve. Once in a while it would operate normally and other times nothing. After replacing the valve last month no more calls. Hopefully it stays that way. Thanks for the replies.