I have been fighting a re-ocurring problem with my HVAC unit. Periodically it trips into a low pressure fault state.
It seems fine now, but it tripped twice the day before yesterday. It is a Miami Heat Pump HPX041V-RF-A heat pump
The only thing I have noticed is around the time it trips, when I am trying to bring it back to life, sometimes the condensor (I think it is the condensor) will kick on, but the fan will not. Or the fan will be humming along fine and just turn off. I cannot reliably reproduce this. I keep the fan in continuous mode. A few months ago they replaced the fan motor. If you are so inclined, you can read about it further if you search posts from my name (I cant link).
The high pressure fault mentioned in the article was unrelated (was the communal roof cooling towers).
Anyways, I had a different company come out.
First he thought the coolant was low, it was sitting at 80ish when it should have been 110?
After further diagnosis though, he thought we had a "TXV valve liquid line restriction".
He showed me with equipment that it was 75-76 degrees below the TXV valve and 47-46 degrees above it.
He said the normal temperature difference should be 8-12 degrees.
They recommend replacing the TXV valve. Does this diagnosis and fix sound reasonable to you all ?
It seems fine now, but it tripped twice the day before yesterday. It is a Miami Heat Pump HPX041V-RF-A heat pump
The only thing I have noticed is around the time it trips, when I am trying to bring it back to life, sometimes the condensor (I think it is the condensor) will kick on, but the fan will not. Or the fan will be humming along fine and just turn off. I cannot reliably reproduce this. I keep the fan in continuous mode. A few months ago they replaced the fan motor. If you are so inclined, you can read about it further if you search posts from my name (I cant link).
The high pressure fault mentioned in the article was unrelated (was the communal roof cooling towers).
Anyways, I had a different company come out.
First he thought the coolant was low, it was sitting at 80ish when it should have been 110?
After further diagnosis though, he thought we had a "TXV valve liquid line restriction".
He showed me with equipment that it was 75-76 degrees below the TXV valve and 47-46 degrees above it.
He said the normal temperature difference should be 8-12 degrees.
They recommend replacing the TXV valve. Does this diagnosis and fix sound reasonable to you all ?