I would like to know the complete theory of operation of this (SURGE) set up!
JP Said it right, your drop leg does not go in the receiver it just shoots by it, this does let you keep the natural subcooling you get outside, its very up this way!
I have two drop legs with check valves that tee together
I think you may have forgot something possibly? do you have an inlet pressure regulator(condenser flooding valve) that is in the drop leg before the receiver and after where the 2 drop legs come together?
Not sure exactly why you have the 2 drop legs with check valves. I guess it is possible that you have a split condenser?? have a look at your discharge line header and see if it goes through a 3 way valve of some sort and then to 2 discharge lines to the condenser.
......then go to a tee that goes to the inlet of the receiver and the straight side of the tee goes on to a solenoid then to the filter/dryer and sight glass then to the liquid header. Obviously the receiver is being bypassed!
the receiver is being passed but it is still open to the system, if you look you should see a pressure reg (DPR/ORD or OPR/CRO)on the top of the receiver that puts discharge gas in to the receiver above the liquid level in the receiver.
What determines when this bypass occurs and what are the set points for the bypass solenoid? Is it energized or deenergized for bypass and is the solenoid the only thing that determines weather system is in bypass or not?
from your first description you note that the drop leg goes to a Tee then on to the header and a solenoid valve is after that tee so i do not see you having a system that can run a surge receiver or conventional receiver, but I'm not going by a whole lot here haha, if you do have a convertible system it would be good to control your surge set up on condenser outlet sub cooling, some more primitive setups use a t stat on the drop leg, but there's no need for that with our fancy schmancy controllers we have on these systems haha. another thing is your drop leg insulated all the way back to the condenser?
Mike