We need to integrate a 30hx chiller thru bacnet thru a open upc module.Looking at some older post I see there's a automapping feature that need to be disabled.And I manually enable the point I want


Q1
Basically how do we do that?

Q2
CCN did not came with rj14 cable is it a standard rj14 cable or a carrier home made with reversed wire?
 
I don't think you need to enable anything on the CCN side.
You'll have to build an equipment file thru equipmentbuilder for the 30hx chiller and download it into the UPC card.
The rj14 cable is a straight thru cable if I remember right.
 
Discussion starter · #4 ·
Open upc was factory installed.
We want to do a integration from what I heard there is a automapping feature that grab 50 point.
Is that right
 
Open upc was factory installed.
We want to do a integration from what I heard there is a automapping feature that grab 50 point.
Is that right
The Open UPC card is already bacnet MS/TP. Just give it an address and discover your points.
 