I had a call for a server room unit, building manager said the display was showing a trip on a pressure switch, and that they had done power shut done the night before.
So I was thinking the obvious one that the power shut down naturally shut down the pumps, wasn't able to transfer the heat to the water, and tripped out on high pressure.
Open up the unit, and it was actually tripping on L.P. Reset everything, started her up, and tripped again withing 30 seconds. Used my electronic detector, no leaks. Then put some solution on anyways just for piece of mind, no bubbles the rest of the time I was there. Coil was spotless, filters were fine, but I removed them temporarily for testing. Evap fan amp draw was bang on, belt was fine, etc.
So when my gauges were on, it would run fine, normal temps/s.h./s.c./ and delta t. Then it would trip out on low pressure regardless. So I just bypassed the l.p. control and it ran as per manufactures specs without issue.
This lp control is mechanical, it's not a digital one, or using thermistors or anything. SAGINOMIYA is the make of it. Just a standard looking control, with no electrical aspect to it aside from the contacts.
I also tried to adjust the cut in and differential just in case it was out of calibration a bit, but nothing I tried would make a difference.
I have a new lp control on order, so basically what my question is,
Has anyone ever seen an issue like this after a power shut down? I don't really get how a shut down could affect a mechanical control like that. So is there something obvious I might be missing? I'm thinking it's just a coincidence with the shut down, but I would rather have a second opinion.
It's an ecoslaire (by dectron)
Model: smfa030gz456fifsciklot
Sent from my SM-G925W8 using Tapatalk
So I was thinking the obvious one that the power shut down naturally shut down the pumps, wasn't able to transfer the heat to the water, and tripped out on high pressure.
Open up the unit, and it was actually tripping on L.P. Reset everything, started her up, and tripped again withing 30 seconds. Used my electronic detector, no leaks. Then put some solution on anyways just for piece of mind, no bubbles the rest of the time I was there. Coil was spotless, filters were fine, but I removed them temporarily for testing. Evap fan amp draw was bang on, belt was fine, etc.
So when my gauges were on, it would run fine, normal temps/s.h./s.c./ and delta t. Then it would trip out on low pressure regardless. So I just bypassed the l.p. control and it ran as per manufactures specs without issue.
This lp control is mechanical, it's not a digital one, or using thermistors or anything. SAGINOMIYA is the make of it. Just a standard looking control, with no electrical aspect to it aside from the contacts.
I also tried to adjust the cut in and differential just in case it was out of calibration a bit, but nothing I tried would make a difference.
I have a new lp control on order, so basically what my question is,
Has anyone ever seen an issue like this after a power shut down? I don't really get how a shut down could affect a mechanical control like that. So is there something obvious I might be missing? I'm thinking it's just a coincidence with the shut down, but I would rather have a second opinion.
It's an ecoslaire (by dectron)
Model: smfa030gz456fifsciklot