Hey, I'm new to this website and happen to be looking though some of the older posting. I would like to clear up a couple of things on the SAMS CO2 store.
1. The store is using 35% propelyene gylcol at +20F fluid temp as the secondary fluid w/404a as the pirmary refrigerant.
2. The low temp system has 404a as the primary refrigerant and CO2 as a secondary fluid w/a supply fluid temp of about -20F. The chillers are standard braze plate heat exchanger and all the components are standard refrigeration componets. CO2 at -20F is around 198psig. Using it as a sencondary fluid you dont have the high pressure of a transcritical system. As long as the DX portion of the system is working your pressure will vary between 198-250PSIG. If you have a DX failure a small aux. heat exchanger with it own condensing unit and eneratogr will kick in until repairs to the DX system are made.
3. CO2 is .50 a pound compared to ~$7.00 a pound for most refrigerants. Also, the thermal properties of CO2 are so much better you only need a 3/8" liquid line to feed a line up of glass doors, but they are using 1/2" for rigidity. With the small refrig line you save money on install (copper only)
4. CO2 has an ODP number of 1 with no global warming portential
5. Since its a secondary fluid there is no concern with oil return.
This is our future they are doing in all over Europe, if they can make it work I'm sure we can do it also.
I enjoy reading all of the other posting it just show we still have some really good talent out there.
1. The store is using 35% propelyene gylcol at +20F fluid temp as the secondary fluid w/404a as the pirmary refrigerant.
2. The low temp system has 404a as the primary refrigerant and CO2 as a secondary fluid w/a supply fluid temp of about -20F. The chillers are standard braze plate heat exchanger and all the components are standard refrigeration componets. CO2 at -20F is around 198psig. Using it as a sencondary fluid you dont have the high pressure of a transcritical system. As long as the DX portion of the system is working your pressure will vary between 198-250PSIG. If you have a DX failure a small aux. heat exchanger with it own condensing unit and eneratogr will kick in until repairs to the DX system are made.
3. CO2 is .50 a pound compared to ~$7.00 a pound for most refrigerants. Also, the thermal properties of CO2 are so much better you only need a 3/8" liquid line to feed a line up of glass doors, but they are using 1/2" for rigidity. With the small refrig line you save money on install (copper only)
4. CO2 has an ODP number of 1 with no global warming portential
5. Since its a secondary fluid there is no concern with oil return.
This is our future they are doing in all over Europe, if they can make it work I'm sure we can do it also.
I enjoy reading all of the other posting it just show we still have some really good talent out there.