Short cycling. When we showed up I did notice the filter/drier was half frosted, and assumed it was plugged being someone replaced the compressor and probably did not use good practices while doing so. Especially it was very obvious that it was not replaced.
I can hear the EEV(or EXV, I use the EEV being that is Russels part name for it, but it kept pissing my partner off when I called it an EEV) working, and going through the menu on the controller it says it was at 62%. When checking the voltages on the board, between pin 1 and 3, it wasnt getting close to what the data was given to us(under 1vdc was what we read), so their engineer told us that board is bad. With a long night for V-Day, 4.5 hrs driving time, I wasnt quite in the mood to stick around when tech support closed. I know that is not a good excuse, but it is what it is, and definitely not the way I normally do things.
We tried to set cut in and cut out to 25/5, but it would keep dropping into a vacuum so we ended up messing with the LPS to keep them running until we can get back. Also disconnected the DTC solenoid(not my call on that one) despite it appearing to be working correct. Top of the compressor was 185f, the DTC is rated for 193f and it was still feeding liquid into the compressor. 8f difference is not awful, but I doubt that is our issue.
I really would have preferred to go by myself, but they have me riding with a guy for the first few days to become familiar with their paperwork. He is a sharp guy, very experienced(supposedly 30 years experience vs. my 9 years), but we do things different. And I, being the new guy, just followed his lead.
The filter drier we replaced was easy to blow through, so I doubt it had a restriction. But being we had to sweat in some Schroeder valves, and the compressor had been replaced, I considered that good practice.
The box was at 7f when we left, but the super heat was still hunting pretty hard. EEV going from 10% to 62%, dropping into a vacuum every few minutes, and being the engineer from Russell said he was certain it was a bad board(we went through the normal checks SH set point, measured SH, and gauged up on the Evaporator and confirmed the board was measuring correct. Refrigerant type was set to R448 in the controllers firmware.
Sorry I dont have more information, but I figured I'd chat it out over the weekend until we get this board being my gut is telling me we will have to tell the customer that we need more parts.
Ugh
-Fred