The duct slide calculator is just that, it is not meant to size ductwork until a friction rate is known to use on the slide calculator.
To find the proper friction rate, one needs to first know the proper size unit by performing a manual J, then select proper size unit using manual S, then design proper duct system by following steps in Manual D.
A residential gas furnace is normally rated at .5 TESP, and most air handlers are normally rated at .3 TESP. If you are testing units with close to one inch of TESP then it is not likely that the system is properly moving design airflow. Most standard furnace PSC motor can handle up to .6TESP and most variable speed units up to .7TESP before airflow is reduced or noisy variable speed blowers.. But on the contrary most airhandlers with PSC motors can handle up to .4TESP and most variable speed units can handle up to .5 before airflow is reduced or noisy variable speed blowers.. Always consult the blower table of the manufacturer to confirm because some units suffer severe loss of airflow at lower statics past the rated static more than others.
I had a PSC gas unit today that was running at 1.11 TESP that had very bad ductwork, this unit had a 3 1/2 ton blower but at 1.11 TESP was only moving about 900 cfm on high. We are going to try to lower the static as much as possible on the return side but the supply is buried in a concrete slab, and customer doesn't want to jackhammer up the floor to fix the supply..lol.. Luckily the A/C is only a 2 1/2 ton and lucky the blower unit is was oversized or the airflow would be too low in current conditions.
Goodluck
J
Learn Manual D inside and out and go to some duct design course and the misteries of duct design will be given, also you will find less than 10% of ducts are truely sized correctly, most are serverely undersized not just boarderline...
On your question if the friction rate that is needed once found by performing a manual D, if the duct needed fall between the prefab sizes then go to the larger size; i.e. needs a 11x22 duct according to the table use a 12x22 duct.