ar_hvac_man, yes there is sight glass and I charged the unit until there was no bubbles. There is no indicator on sight glass.... Just one of them cheap ones that u can see liquid. My superheat was 11.. I didnt check subcooling.... I hope I did that right
Basically you did it right. Charging to a clear sightglass indicates you have attained a liquid seal at the outlet of the receiver.
How can you charge it without checking sub-cooling if it has a TXV ? And every sight glass I've seen changes colors to indicate moisture.
It's true most sightglasses have a moisture indicator, but their primary benefit is to provide a visual indication of the state of charge...if you're doing refrigeration.
On larger refrigeration systems with a receiver, subcooling is meaningless as a charging metric.
You MUST have a full sightglass proving a liquid seal in the receiver.
I agree with this wholeheartedly.
In addition...
In my experience, I have followed behind some good A/C techs who, although apparently knowledgeable about how to charge a residential A/C system with a TXV, failed to see the difference in a typical commercial refrigeration system with a TXV & receiver and how it works.
Most of these techs have been taught to ignore the sightglass and go directly to subcooling as the correct measure of system charge...because that's what's indeed required of a resi A/C with TXV. They know that when more refrigerant is added the SC will increase and vice versa. What they fail to think about is why this occurs.
When refrigerant s added to a resi A/C system with a TXV the added refrigerant starts to stack up in the condenser coil resulting in increased subcooling at the condenser coil outlet. With a refrigeration system with a receiver and TXV, this doesn't hold true.
With a refrigeration system with a receiver added refrigerant will tend to end up simply filling the receiver with no additional stacking of liquid in the
condenser coil...and so, no additional subcooling. The typical refrigeration system will only give you around 5 Deg F subcooling and that's it. Once the sightglass clears, what you see is what you get.
What would you need to do then to achieve 10-15 Deg subcooling with a refrigeration system?
You would have to charge until the receiver were 100% full at which point the refrigerant would begin to stack up in the condenser. At that point you would see an increase in subcooling.
But of course, if the system is controlled on pumpdown to cycle off you'd be called back for a system which tripped the high pressure safety.
I once had a call on 5 HP system on a walk-in at a convenience store where I had to remove about 40 lbs of R401A because the previous servicer (an A/C contractor) had noted on the unit that it must be charged to 15-20 Deg subcooling.