Came upon a R22 walk-in cooler today at an indiapendant convenience store. According to them a few months ago someone came in and stole all of the copper off the unit and the unit was left open for well over a week. Not an accurate timeline but it's hard to get a complete story. Well they had someone come in and re-pipe the system and charge it up.
Now a month later I show up for a call saying the unit is tripping the breaker. Reset the breaker and go out to start the unit to see if I can get any indication as to why it's tripping the breaker. First time flipping the disconnect at the unit nothing came on and tripped the breaker on the panel inside. Reset the breaker and disconnected the ultra start that someone put on it to replace the potential relay on the unit. Flipped the disconnect and cond fans and comp came on pulling LRA so I shut it off. Reconnected ultra start and flipped disconnect and comp and cons fans both came on.
Suc 60
Head start off around 275 and rise.
Amps start off at 17 and rise.
So after the unit ran for a good min or two I noticed the head was steadily rising and got well over 400psig and was still rising. The amp draw went from 17-23. At this point I shut the unit off. I checked the cond coil for debris and it was fairly clean. I'm not sure how to check for discharge air recycling but it could be possible on this unit with it's covering.
Next thought was non condensables so I disconnected the compressor and let the fans cool the cond coil. Waited for dschg and LL to cool and took readings and both were at 92.8-93 as was air entering the cond coil. Pressure for the coil was at 185 with a saturation of 96. According to the test I should have been down around 174-175psig.
Can I get some thoughts on my readings and diagnosis? Much appreciated
Sent from my iPhone using Tapatalk
Now a month later I show up for a call saying the unit is tripping the breaker. Reset the breaker and go out to start the unit to see if I can get any indication as to why it's tripping the breaker. First time flipping the disconnect at the unit nothing came on and tripped the breaker on the panel inside. Reset the breaker and disconnected the ultra start that someone put on it to replace the potential relay on the unit. Flipped the disconnect and cond fans and comp came on pulling LRA so I shut it off. Reconnected ultra start and flipped disconnect and comp and cons fans both came on.
Suc 60
Head start off around 275 and rise.
Amps start off at 17 and rise.
So after the unit ran for a good min or two I noticed the head was steadily rising and got well over 400psig and was still rising. The amp draw went from 17-23. At this point I shut the unit off. I checked the cond coil for debris and it was fairly clean. I'm not sure how to check for discharge air recycling but it could be possible on this unit with it's covering.

Next thought was non condensables so I disconnected the compressor and let the fans cool the cond coil. Waited for dschg and LL to cool and took readings and both were at 92.8-93 as was air entering the cond coil. Pressure for the coil was at 185 with a saturation of 96. According to the test I should have been down around 174-175psig.
Can I get some thoughts on my readings and diagnosis? Much appreciated