I had a Trane XR13 unit (2TTR3036A) installed yesterday along with a Trane 13 seer evaporator coil (2TXCB036A) and Trane XR 80 single stage furnace (TUD1B080A9361A). The system was up and running at 1pm. At that time, the temp at the outlet ducts was measured at 65 degrees. At 5 pm when my wife returned to the house, there was no cool air coming out of the vents, only warm air. The unit ran for another two hours until 7 pm when I returned home and turned off the system. When the tech returned this morning to check on the problem, he determined the system was overcharged with freon. The condensor, which ran for about a 1/2 hour prior to the tech's arrival was hot and had to be cooled down with a hose. The tech told me the pressure was 275 and should have been around 225. He said he removed 1 and 1/2 pounds of freon and said the condensor is now running properly. He also said the condensor was not permanently damaged and it is designed to shut down when it gets too hot. Is the situation I generally described likely to cause the condensor to be permenantly damaged? Also, the tech said the unit comes precharged. Was the fact that it was installed and operated in this apparant overcharged condition a Trane issue, an install issue, or both? Thanks in advance for your comments.
Mike