Have an old Carrier 5H-60 open drive compressor with a 50 HP 1750 rpm motor. Unit was overhauled 2 years ago, on old ACME chiller. Getting high motor amperage rated for 110 amps running at 124-125 amps full load and if head pressure gets up over 270psi amps will go up to 150... Checked voltage and phases ok, adjusted water regulator to keep 200psi or so head pressure ok, running low suction around 50psi give or take. Load is very low on this chiller. Would like to adjust internal unloader but cant find any info on this old puppy. Called local Carrier they want to mail me an manual but that will take a week or so. Motor was also rebuilt last year with compressor.