Manitowoc SD0452A

1 reading
3.2K views 2 replies 3 participants last post by  hvac wiz 79  
#1 ·
Worked on this machine today, found bad circuit board, unit would not
go into harvest, relpaced board, normal operation, wondering how common
this problem is,any of you fellow techs have this problem? thanks
 
#2 ·
On the Manitowoc S-Models, I have found more bad circuit boards than I have found on the Q, J or B-Models. I think the S-Model board is of lesser quality than the others were.

Jabs
 
#3 ·
i see alot of S machines & have only replaced one board .. per manitowocs recomendations ... all others have issues relating to the water system .. most with the water level light illuminated but trough is empty & i receive alot of false calls .. most for water curtain being stuck open .. either by magic as its not being held open by anything, or during harvest ice sheet breaks apart & little pieces hold curtain open, & ive seen ice from a regular full bin take a very long time to melt preventing freeze cycle .. after discussing this with many of my customers & telling them what to look for .. ive been told i have saved alot of them from calling me for no reason
 