Hi guys! I had a 'no-ice' call yesterday on Mani Q-series, remote air-cooled, obvious reason was a old and rusty dump valve, so replaced it and machine started to work again, made ice but didn't drop, machine shut itself down after 3.5min max harvest. So I checked evap - nice and clean, has coating, no separation, then decided to put my no-hose gauges on - good pressures while in freeze mode(50/260, all corresponds to water and air temps in manual charts). But after ice probe calls for harvest, I hear a click, pressures start to somewhat equalize, but then immediately they go to 50/260, and low side slowly goes down. So looks like harvest solenoid opened but closed right away? i have very limited experience with ice machines, so could you please give me a hint? Board? Harvest solenoid valve? Thanks!