Helped change a air handler out last night due to a leaking coil so I'm not certain the unit didn't have pressure issues before, pulled vacuum down to 475 and held it there. Added about 14oz of POE oil, weighed in 7lbs of 407c inverted and started the unit up only to see the pressures we're about 39 psi and 103psi. Both the suction and the discharge line were cold. Does anyone have an idea what is going on?
Do you any superheat or subcooling numbers?
Do you have what amps the compressor was pulling and its RLA?
TXV or fixed metering device?
Was a new filter drier installed?
Is it a straight AC or Heat pump?
What is the name plate refrigerant charge?
Did you remove all the compressor oil and add all new POE, or just add 14oz of extra POE oil on top of what was in the compressor?
What was the IDDB, IDWB, ODT?
What were the Return and Supply air temps?
What is the model number of the outdoor unit?
We are working blind here with only system pressures. Please paint a better picture of what you are dealing with so we may be able to provide the some insight into the issue you are having.