1 - 6 of 6 Posts
cleancondenser
· Registered
Joined
Discussion starter · #1 ·
JCI has Digital Controller (DX-9121) series
It is LONMARK certified .
It appears to be the next line of DX-9100 controllers
What does it mean when they say it is LONMARK certified
It appears it has no need for Network variables since
all its inputs and outputs are all locates in the same controller
Thank You
The DX-9121 controller is a Johnsonized version of Lon called N2E which only allows peer-to-peer between DX-9121s (no Neuron ID). If you want a version of DX that is actually LON that can communicate with other LON devices you need the DX-9200. The DX-9200 actually has a couple different versions that fit different LON functional profiles. Documentation is on JCI website. http://cgproducts.johnsoncontrols.com//MET_PDF/1162250.PDF
Here is the explanation of the Lonmark Certification in the JCI literature for the 9121:
"The Version 3 controller has been approved as a LONMARK device and
conforms to the LONMARK specification for network data transmission."
Which essentially means that it is N2 communications over a LON trunk, without the features of actually being LON.
Discussion starter · #4 ·
Thank you for the good Link
We are trying to integrate more LonWorks controls into our sites
Most of this is done thru Johnson ,because that is where we have
the most freedom
Unfortunately Johnson does not always offer
us much help with LonWorks because they
tend to favor Bacnet and a little of FX-40
Which I think is superior to LonWorks
But, we are trying to keep everthing up to date and balanced
Our local Johson branch and their vendors (I won't mention names)
Tend to be slow and un knowing when it comes to LonWorks
1 - 6 of 6 Posts