X2^^^ do some tests and checks don't guess
I can only guess at this point, I'm not the contractor. Been out of the field since 2012. I'm in facilities management. I'm confident his diagnosis is incorrect. Just wanted some other opinions. I don't want to spend money I don't have to and I want this fixed properly without chasing tails.
 
Save
What's the MasterBilt model for this cooler? The current BMG series apparently have an air sensing thermostat and no defrost timer. If this unit is the same, I'd cut add a defrost clock before I spend a lot of time and money on it.
 
Save
Got a coil model number ? How is the refrigerant circuit configured ?
From the pitch on the blades the fans are pulling thru the coil.
That's a blow through coil...the fans are pushers, blowing the air to the back of the case.
 
Save
Look at the pitch on that blade on the left near the bracket. That blade would have to be reversed to push air.
That blade looks like its drawing air through the coil while the blade to the right of it looks like it's pushing. Not that that's the case but didn't someone mention the air could be cavitating:LOL:
 
The fan blade is concave on the coil side and pitched for CCWSE rotation. The airflow is definitely blowing through the coil.

 
Save
All of them are the same.

Look at the different colors...ie, white grey and black. The white is looking though the opening to the white of the cabinet beyond. The grey is the fan blade itself and the square black in the center is the shaft sticking out.

The viewing angle of the center one clearly shows the concave curve of the blade.
 
Save
If that's actually two coils, with two sets of metering devices and distributing tubes where the ice is building up, my vote would be under feeding for whatever reason. Bad/wrong metering devices, cold ambient / low head, low charge, etc.

Is this a new installation? What I'm really trying to ask is, did it used to work several months ago? If so, something changed. If not, is the equipment sized proper, could be an undersized condensing unit if it is a new install; running non stop but just cold where the refrigerant is feeding the coil.
 
Save
Discussion starter · #34 ·
What's the MasterBilt model for this cooler? The current BMG series apparently have an air sensing thermostat and no defrost timer. If this unit is the same, I'd cut add a defrost clock before I spend a lot of time and money on it.
TEM 430
 
Save
Discussion starter · #35 ·
Here's another pic. Seems to be the far end of the coil, not where the metering device enters
 

Attachments

Save
The more I look at the pics, the more I'm seeing the result of lower airflows as you get further away from the fans...ie, uneven airflow cross the coil. Then you add repeated incomplete defrosts over a long period of time and you eventually have these ice formations.
 
Save
Yeah, judging by those rust marks, it's been going on for quite awhile.


The more I look at the pics, the more I'm seeing the result of lower airflows as you get further away from the fans...ie, uneven airflow cross the coil. Then you add repeated incomplete defrosts over a long period of time and you eventually have these ice formations.
 
Save
Bottom right of the coil looks thicker..and gets thinner as it approaches the top.. and the rust formation deff makes you think it's an airflow issue..coldspot forming at farthest point of coil, no transfer of heat, colder ambient

Sent from my SM-G900V using Tapatalk
 