My apologies for the length of the post, wanted to make sure I gave you all of my efforts to date. Went out on a no heat call Sunday… Walked up on the furnace ran it through the start-up sequence for heat. Inducer Fan starts but no hot surface igniter.
Troubleshooting Steps:
At this point, I’m thinking system board, except the “#$#5” thing starts every theI bypass the pressure switch.
Any thoughts, suggestions, verbal beatings -
Troubleshooting Steps:
- Jump out the pressure switch, furnace starts on every try for the next 10 cycles
- Check voltage (122v) to the inducer fan/amps (~1 amp)/resistance (0 ohm) – no issues other than motor is noticeable loud intermittently.
- Check vacuum port from inducer motor using manometer (.8 - .75 w.c.) running for 1-2 min.
- Check Pressure switch (.50 w.c.) – connect meter and check resistance when inducer starts. Switch opens but there is some resistance reading
- Pull the flu pipe off of the inducer to check for anything in the flue and restart inducer without flue connected to bypass any possible blockage. No improvement
- At this point, I have a system that starts every time when the pressure switch is bypassed, so I install a new pressure switch – new one ohms 0 when it opens and system starts a couple of times in 5-6 cycles, but issue is still intermittent.
- Next, I pull the vacuum hose off the inducer, with the inducer running the system starts every time that I manually pull the hose and replace it on the inducer port, so I replace the inducer motor assembly – thinking with intermittent noise and play in the motor shaft may be causing some operational issues.
- After replacing inducer motor and pressure switch, system starts every time for 10 cycles.
- Next Day, customer calls saying everything worked great for the remainder of the day, but house was cold next morning… system doing the same thing.
At this point, I’m thinking system board, except the “#$#5” thing starts every theI bypass the pressure switch.
Any thoughts, suggestions, verbal beatings -