I've been in the controls business for over 35 years. More than half my life. Lately I'm seeing things that are now scaring the $hit out of me.
Lets start the list with Heat pipes that have 24 VAC solenoid Valves wired in parallel which draw an inrush current of 3.4 amps each with a holding current of 1.2 amps. No problem until you have about 30 or so of these valves setup for three stage control. The installing electrician spent a few days trying figure out why the circuit breaker on his 75va transformer was tripping. Ended up installing a 2 kVa 24VAC transformer, conduit for the increased wire size. Of-course the control guys get stuck with supplying 30 amp contactors.
How about the Daikin BACnet interface with 100 or so FCU's connected. 2900 points don't mean a thing when the Daikin start-up guy didn't bother to keep track of which address he assigned to a room FCU.
A primary variable speed pumping system with bypass valve that's supposed to maintains minimum flow through a Chiller piped from the pump discharge pipe to the chiller discharge pipe. Engineer was worried the return water would get to cold comming back. Solution close and disconnet bypass valve, Install 3-way valve at largest AHUs.
Don't even get me started on Multi-Compressor Colmac heatpumps with Carel controllers.
Please feel free to add to list. I cannot believe I'm the only one suffering in PC crap world.
Lets start the list with Heat pipes that have 24 VAC solenoid Valves wired in parallel which draw an inrush current of 3.4 amps each with a holding current of 1.2 amps. No problem until you have about 30 or so of these valves setup for three stage control. The installing electrician spent a few days trying figure out why the circuit breaker on his 75va transformer was tripping. Ended up installing a 2 kVa 24VAC transformer, conduit for the increased wire size. Of-course the control guys get stuck with supplying 30 amp contactors.
How about the Daikin BACnet interface with 100 or so FCU's connected. 2900 points don't mean a thing when the Daikin start-up guy didn't bother to keep track of which address he assigned to a room FCU.
A primary variable speed pumping system with bypass valve that's supposed to maintains minimum flow through a Chiller piped from the pump discharge pipe to the chiller discharge pipe. Engineer was worried the return water would get to cold comming back. Solution close and disconnet bypass valve, Install 3-way valve at largest AHUs.
Don't even get me started on Multi-Compressor Colmac heatpumps with Carel controllers.
Please feel free to add to list. I cannot believe I'm the only one suffering in PC crap world.