Have some racks that are all doing the same type of thing. They are what we call "Hybrid" but its closely related to the Tyler "Enviroguard".
How it works. Critical charge rack (of sorts). The receiver is not a receiver, its more of a surge tank to dump excess gas from the system when conditions provide too much sub-cooling. We run a head of 155psi R-507. 99.9% of the time the "receiver" is 0%. We take advantage of the sub-cooling for efficiency.
DDR (Defrost Diff) for HG defrost. 25psi ?t on defrost. HG will go reverse flow and return via LL and dump into the "Saturated liquid return" header. Then go into the Condenser disc line just before it goes up to the roof.
Here is our problem. When nothing is in defrost the "Saturated liquid return" will be full of liquid (due to design of check valves in that direction). But we are getting the liquid flooding into the condenser disc line and not just a little. enough that the line is cold right after the tee. So we installed a solenoid on the "Saturated liquid return" line before the sight glass that will energize with the DDR goes into diff mode (with a 20psi diff check around it in the same direction to prevent making a bomb).
I have noticed that we are getting a diff of about half a psi to a full pound around the disc check valve. I went as far as to pull the guts out of one to see if it helped, it did not. We were still getting liquid migration. Now I dont have a problem living with a sol in the "Saturated liquid return" line, I just dont want this to be a bandaid.
(this problem is occurring on racks from new to 5 years old. All different in how the 7/8" "Saturated liquid return" ties into the disc line. I thought about venturi effect but this is not the case.)
I am open to ideas here... I am stumped as to why we are getting flow. (obviously its due to gas going from a higher pressure to lower, we are talking less than a psi, I know the physics.)