Ongoing problems with Trane 5-burner natural gas furnace new circa 2002. First day running this season I noticed cold air blowing. Lockout code (2 flashes). Restarted and heated at call for heat but stopped short of temp goal, then lockout again. Putzed with this for a day or two and then no gas at all. From reset (power off, power on) this is what happens when there is a call for heat:

1)inducer runs
2)hsi glows
3)"click" from solenoid in control board, 27 volts to gas valve
4)no gas that I can discern
5)hsi dims
6)inducer stops within a minute or two

This cycle will continue 2 more times then 2-flash lockout

The fact that there is a click and 27 volts to the gas valve *at the correct time* should mean that flame sensor, limiter and inducer pressure are all satisfying the board. So I tested the w.c. at outlet and got 3.3. I adjusted to printed spec of 3.5. Had no effect. I installed a new gas valve. No effect. Tested w.c. *inlet* on new gas valve, 5.5 which is at the low end of things but I've never read anything that says the valve won't operate with lower than 7 w.c. inlet pressure or anything. I have read that low inlet pressure causes problems, suggesting that gas valve would continue to work. When the gas was working in the limited fashion that it was it was a robust flow to the burners. I could increase the inlet pressure by shutting the water heater and stove but this really shouldn't change anything. From a purely intellectual standpoint, does anyone have any theories as to what the problem might be?
 
Your listed as a homeowner.
What does your service technician suggest to fix the problem?
 
Save
Discussion starter · #3 ·
Your listed as a homeowner.
What does your service technician suggest to fix the problem?
well ... I haven't called a service tech. I posted here because i didn't want to wait for the guys at the dyi site to respond. Besides, I've done all the work already. Turns out it starts after one or two tries. It's running right now.

As to why it does this short-cycle-y kind of thing and sometimes locks out ... I really don't know based on the things I wrote originally. There could be some really subtle thing I'm missing like not enough vacuum on the short cycle tries and maybe the inducer is starting to fade. It sounded like a dump truck last year but sounds ok now, so the bearings have been through some changes i expect. If it keeps working I'll worry about it when it messes up again.
 
Unfortunately we can’t offer any DIY instruction here. Per the rules you agreed to when you joined. Please note the bright red banner at the top of the page.
 
Save
You have to post in the Tech to Tech section .... you posted in the AOP section ( where tech advice is not allowed )
 
Save
You have to post in the Tech to Tech section .... you posted in the AOP section ( where tech advice is not allowed )
He's not a tech, so his post belongs here.

This is not a DIY site no matter where he post it.

Thread closed.
 