I got a Air handler that has a steam coil mounted horizontally and was told the coil is not draining.
I have witness it in action. after a few hours of operation the discharge temp drops from 130 down to 80.
the steam pressure and heating valve remain the same 5-10 psi and valve wide open.
the only way the operator can get it to work again is to "drain it" he closes the hand valve then drains the circuit at the strainer before the steam trap.
We had a few contractors look at it, the even replaced the trap and strainer.
Was told the only way to get this to ever work is to angle the coil inside the air handler to help it drain.
Odd yes?
I have witness it in action. after a few hours of operation the discharge temp drops from 130 down to 80.
the steam pressure and heating valve remain the same 5-10 psi and valve wide open.
the only way the operator can get it to work again is to "drain it" he closes the hand valve then drains the circuit at the strainer before the steam trap.
We had a few contractors look at it, the even replaced the trap and strainer.
Was told the only way to get this to ever work is to angle the coil inside the air handler to help it drain.
Odd yes?