I just installed a new Goodman 13SEER 2.5Ton R410a (scroll) fixed orifice system with new air handler. Correct oriface was installed. Out side temp is 93F indoor is 73F. Low side pressue fluctuated 132-136psi. Low side temp is 58.6F giving me a superheat of 17.4. Calculated super heat is 14. Not far off. The high side is fluctuating from 450-650psi. I have not seen this before. I can hear the compressor labor at the higher pressure. My boss said not to worry about it unless the customer calls. I think the compressor may be damaged by this high pressure. Any thoughts out there?