Hi GoCougs and R600a:
GoCougs your comment was that they (CoreMax) suck. If you don't mind I would like to understand what it is about them that makes you say that and compared to what. I'm not trying to be defensive or anything just genuinely trying to understand your situation/experience. Obviously we want to make the highest quality product that is easy to use for not only the manufacturer (be it Goodman, Carrier, Trane, etc. all of whom have used them for many years) but also for the service people that work with them in the field. When I hear someone say "they suck" that's a problem that as a manufacturer who cares about what you, our customer, thinks I want to give you an opportunity to help me/us understand what is happening so that we can make our product, training or whatever better. That is where I'm coming from and I hope that you will help.
A bit more detail on the CoreMax system... CoreMax was designed to provide significantly more flow than a Schrader valve (3 to 5 times more) for faster evacuation and charging in addition to better/more robust sealing performance. It absolutely does that and there is abundant test data verifying it. That's why the manufacturers use them. It has proven to save them significant time on the manufacturing line. Also, the design of the CoreMax has demonstrated them to be more leak tight because there is a metal to metal seal between the valve core. The CoreMax design is quite different than Schrader but it's subltle.
In order to get a leak tight seal it is important that the valve core and seat sealing surfaces be free of contamination and that the valve core be tightened to the proper torque value of 8 ft-lbs! The core tools SCFT10 or SCFT20A have a hex on the end or the TEE handle to which you can attach at torque wrench and we also offer a preset wrench (SCFTM01) that is available for purchase.
CoreMax also features the same SAE 1/4 flare with a 7/16-20 thread that a Schrader fitting typically has so that common refrigeration hoses can easily be connected, i.e. you can evacuate the system or add/remove refrigerant to the system by connecting common refrigerant hoses to the CoreMax valve.
With that said
a Schrader core removal tool will not work with CoreMax because the design of the CoreMax is different than Schrader so if you want to remove the CoreMax core for whatever reason you must buy/have one of our tools, either the SCFT10 or SCFT20A tool with the SCFT20A being better suited for field service because you can as I said in my previous post exchange a CoreMax core without losing refrigerant with that tool. The process of replacing a CoreMax core is very similar to how you do it for a Schrader but you need the CoreMax tool, e.g. SCFT20A.
If the factory has its process under control and is not introducing contamination into the seat before the valve core is installed then a good, reliable hermetic seal should be achieved and leakage through the CoreMax should virtually zero indefinitely (As I noted before CoreMax has demonstrated itself to have less leakage than Schrader many times). Also it is recommended that a brass (preferably) or plastic dust cap be screwed onto the CoreMax to protect it from debris/contamination and also provide a secondary back-up seal.
What happens after it leaves the factory is where you as service technicians experience it. Contamination on sealing surfaces is the enemy of and valve regardless of whether it is a CoreMax, a Schrader, a Packed Angle valve, whatever. It is my guess that in the case of CoreMax that when you experience a leaking Core it's due to contamination somehow getting into the sealing area, either from inside the system during evacuation or from outside the system when refrigerant is being added when there was contamination in the top of the CoreMax (or Schrader) that was not blown out before the refrigerant "pushed" it through the valve.
As I said previously, I/we would like to better understand your situation and see if we can change your opinion. We are also happy anytime to provide training or discuss questions you may have and help solve any problems.
I/we would like to hear from everyone who has had any issues or would like to give feedback with our CoreMax system!!! Please feel free to contact me directly at 651-251-9741 or at my e-mail
thomas.braun@fastestinc.com or through our 800 number (800-444-2373).
Thank you!