We've been having problems with our 1.5 ton Goodman heat pump icing up. It tends to frost up badly on the bottom, but the top 60% of the fins are completely clear.
Originally this heat pump was mated to an R22 air handler. I think the previous homeowner decided to replace the outdoor unit without realising he should have replaced the air handler as well. We replaced the air handler last year. After installation there was some concern that there might be a restriction in the coil due to the R22 oil, as the high pressure was too high and low pressure was too low.
This winter we noticed it icing up again. The HVAC company found the refrigerant was low, and added 2lbs along with some leak sealer. Pressures were ok after, so they don't think there is a restriction. A month later it was still icing up at the bottom again, and they again found it about 1.5lb low. They topped it up again, and found the leak in a service valve, which is now repaired.
The problem is, it's still frosting up at the bottom just a few days later, so I suspect the frosting is unrelated to the leak.
I just want to get some opinions before spending more money on this.
Could there be a restriction in the coil where it's starting to ice up? Would the pressures look normal if the restriction is partial and enough time has passed since starting the compressor for the pressures to equalise before and after the restriction?
The system is set up for 30 min defrost with the delay setting, and defrost seems to be working fine on the top half of the coil. Entire coil does completely defrost when I switch to A/C for 20 mins.
Originally this heat pump was mated to an R22 air handler. I think the previous homeowner decided to replace the outdoor unit without realising he should have replaced the air handler as well. We replaced the air handler last year. After installation there was some concern that there might be a restriction in the coil due to the R22 oil, as the high pressure was too high and low pressure was too low.
This winter we noticed it icing up again. The HVAC company found the refrigerant was low, and added 2lbs along with some leak sealer. Pressures were ok after, so they don't think there is a restriction. A month later it was still icing up at the bottom again, and they again found it about 1.5lb low. They topped it up again, and found the leak in a service valve, which is now repaired.
The problem is, it's still frosting up at the bottom just a few days later, so I suspect the frosting is unrelated to the leak.
I just want to get some opinions before spending more money on this.
Could there be a restriction in the coil where it's starting to ice up? Would the pressures look normal if the restriction is partial and enough time has passed since starting the compressor for the pressures to equalise before and after the restriction?
The system is set up for 30 min defrost with the delay setting, and defrost seems to be working fine on the top half of the coil. Entire coil does completely defrost when I switch to A/C for 20 mins.