I have been looking into geo thermal heat pumps and the options with vertical vs horizontal loops. If the ground is always 55 degrees F, then in theory you have 55 degree water coming in from the ground, and 68-80 degree water coming from inside the house, depending on how warm it is.. Assuming that you size the loop to have enough heat transfer with the ground to actually cool the water to 55 degrees F, it should work, right?
So,
1. would it be possible to put in several bore holes, or some long horizontal loops in the ground.
2. Run High Density Poly Urethane tubing in them.
3. Add grout, or don't add grout..
4. Cascade the loops together back near the forced air gas furnace into one big loop.
5. Construct or modify an evaporator heat exchanger for the forced air system so that it circulates not refrigerant, but just water with antifreeze in the geo tubing loops.
6. Put a pump in the middle.
So now you have a cooling only Geothermal system that only costs the amount of energy to run the pump.
Seems like it would work just fine?
What are your thoughts?
In a typical geothermal system, I've been seeing them recommend one 150-200 foot bore hole per Ton of cooling. A 2.5 ton system like my house would require might take 3 bore holes 150 feet each if I was using a compressor system.
In a compressor system, what is the temperature of the water going into the ground measured right after the compressor, and what is the temperature coming out of the ground after going through the geo loop? I assume it doesn't get all the way down to 55 degrees F..
I assume in my method, I might need twice the bore holes to get the same performance of cooling, but even still, it should be more efficient, because you're not running a compressor..
-Jeff
So,
1. would it be possible to put in several bore holes, or some long horizontal loops in the ground.
2. Run High Density Poly Urethane tubing in them.
3. Add grout, or don't add grout..
4. Cascade the loops together back near the forced air gas furnace into one big loop.
5. Construct or modify an evaporator heat exchanger for the forced air system so that it circulates not refrigerant, but just water with antifreeze in the geo tubing loops.
6. Put a pump in the middle.
So now you have a cooling only Geothermal system that only costs the amount of energy to run the pump.
Seems like it would work just fine?
What are your thoughts?
In a typical geothermal system, I've been seeing them recommend one 150-200 foot bore hole per Ton of cooling. A 2.5 ton system like my house would require might take 3 bore holes 150 feet each if I was using a compressor system.
In a compressor system, what is the temperature of the water going into the ground measured right after the compressor, and what is the temperature coming out of the ground after going through the geo loop? I assume it doesn't get all the way down to 55 degrees F..
I assume in my method, I might need twice the bore holes to get the same performance of cooling, but even still, it should be more efficient, because you're not running a compressor..
-Jeff