Working on 22 year old rheem heat pumps. There are 4 systems. I just took over the work at this daycare for the HVAC. I have no background information on previous work other than what I gathered as I looked it over. I noticed 2 systems both freezing up at the accumulator up to the compressor and back to the reversing valve and slowly down the suction line. My suction pressure for both systems is right at 50psig. These are capillary tube systems. My suction line temp hovers between 27-35 degrees. My superheat averages 5 degrees. My first thought was that there is an airflow issue. The blowers all are single speed and appear to all be running exactly the same. I checked the capacitors and they were fine. I replaced every filter and checked all the evaporator coils. I cleaned all the condenser coils. On 1 system I backed refrigerant up and opened up the metering device at evaporator. Black. So I cleaned it up. Vacuumed system down and added acid away to the system. I discussed with owner of daycare to remove all refrigerant but that was too expensive. I was told to try the acid away first. So I did. That one particular system now intermittently freezes up in same spot at compressor/accumulator/etc.. I have done nothing to the other system that freezes up really bad at compressor/accumulator/etc.. The outdoor temperature was around 70 degrees as well as the indoor temperature. Humidity outside was around 47%. I do not know indoor humidity. And with the airflow I checked all fire dampers to make sure they were open. I just dont see this being a refrigerant problem. If it was undercharged my line would not immediately be freezing cold on start up. If it was overcharged I would expect to see much higher condenser pressure. My high side was around 220-225. So what do I do to fix this issue? Is there so much contamination in the system that it is now reduced system capacity? My solution would be to remove all refrigerant. Flush. Nitrogen. Evac. Weigh in charge. But expensive. Especially if that doesn't work.