penderway, KindaSorta, on a 50' LL, going up 30' ,5' horizontal outside, and 15' H in the attic, where does the "not full LL begin" ? Not a joke, I don't know.
Terry, your logic is sound. The ideal situation if for all metering devices is to be fed a full column of liquid. This way the operation is very predictable.
But, with fixed orifice systems (omitting refrigeration units with liquid receivers) the charge is considered critical.
Meaning that the amount of refrigerant keeps the compressor cool enough but without ever flooding it. It needs to do this over the entire range of conditions the compressor is designed to operate in.
The Carrier fixed orifice superheat chart is used to ensure that this is achieved. Proper superheat when the humidity is high assures the proper superheat when the humidity is low. Compressor always stays cool enough, and without ever flooding.
I have observed that under conditions where the superheat is required to be low, the evaporator is pretty full but the condenser not so much... so no subcooling happens. The refrigerant leaves in a saturated state. Without any means of further cooling... the fixed orifice receives bubbles.
This is by design and considered a fair trade off for a simple, less expense metering device with increased reliability.
Plenty of FO systems have had compressor failures due to charging it to a full sight glass instead of the target superheat.