Low Ambient Operation
What are you going to do about low ambient operation? A Trane Voyager we have, during low ambient, compressor is locked out thru the O.A. sensor which is part of the economizer. You'd have to add head pressure controls, above what the unit already has and put another low ambient control for a lower setting.
Does anyone have the instuctions for the Economizer Module, Trane P/n MOD01670 Honeywell P/n W7399B1002 ? Also, what test resistor do you use to put the unit into Econmizer test mode? Do you leave it hooked up, or momentary contact it to test terminals ? Everything seemed to work after I replaced OHS, and Module, but was getting bums rush to get off job.
BTW all decals, booklets have been stripped out of this unit. Their quest for job security didn't work so now I've got the unit.
RTU Unit I.D. ____R 1_____ Manufacture ______Trane______
M/n ____TCD420AE0R2A7FE5AB0D0F0HJ000000______
S/n ____C05E04734__________________________________