I recently had a new 15 SEER 3-ton Carrier Infinity CAC system installed. In order to qualify for a rebate with my local electric company, the installer filled out a form concerning the A/C's performance. Here's what is listed:
AIRFLOW:
Amps -- Compressor: 29
Amps -- Furnace: 9.0
Return db Temperature: 67.2
Return wb Temperature: 59.1
Supply db Temperature: 54.3
Supply wb Temperature: 48.2
Actual temperature split (return db - supply db): 12.9
Target temperature split: 20
Difference: 6.1
TXV System:
Liquid line pressure: 266
Liquid saturation temperature: 86
Liquid line temperature: 70
Actual subcool (liquid saturation - liquid line): 16
Target subcool: 14
Difference: 2
Now, I've got a couple of concerns with the airflow information:
1. First and foremost, the difference between the actual temperature split and the target temperature split is 7.1 and not 6.1. I don't know if that was an unintended error or was done purposely by the installer on the form.
2. I've read in various sources online that the difference between the actual temperature split and the target temperature split should come out +/- 3, but in my case it's 7.1. What exactly does that mean? (I know little about A/C, I just worry when I see that the actual split is so far off from its target). Does this mean that the system does not have proper airflow? Was something done incorrectly when it was installed? Is the system not functioning within manufacturer's specifications? What can/should be done to remedy this "problem" (if it's even a problem at all)?
Thanks in advance for any thoughts or suggestions.
AIRFLOW:
Amps -- Compressor: 29
Amps -- Furnace: 9.0
Return db Temperature: 67.2
Return wb Temperature: 59.1
Supply db Temperature: 54.3
Supply wb Temperature: 48.2
Actual temperature split (return db - supply db): 12.9
Target temperature split: 20
Difference: 6.1
TXV System:
Liquid line pressure: 266
Liquid saturation temperature: 86
Liquid line temperature: 70
Actual subcool (liquid saturation - liquid line): 16
Target subcool: 14
Difference: 2
Now, I've got a couple of concerns with the airflow information:
1. First and foremost, the difference between the actual temperature split and the target temperature split is 7.1 and not 6.1. I don't know if that was an unintended error or was done purposely by the installer on the form.
2. I've read in various sources online that the difference between the actual temperature split and the target temperature split should come out +/- 3, but in my case it's 7.1. What exactly does that mean? (I know little about A/C, I just worry when I see that the actual split is so far off from its target). Does this mean that the system does not have proper airflow? Was something done incorrectly when it was installed? Is the system not functioning within manufacturer's specifications? What can/should be done to remedy this "problem" (if it's even a problem at all)?
Thanks in advance for any thoughts or suggestions.