Discussion starter · #1 ·
Can anyone tell me the benefits or difference between a direct vent furnace setup compared to non-direct vent furnace? With direct vent would this eliminate the stale/stuffy air during the cold winter season? I bought a Goodman GMH95 series and before the installation I am considering is the modification to direct vent since my old furnace does not have this setup.
 
Direct vent will not eliminate stale stuffy air feeloing.

Done as a proper 2 pipe system, it won't draw cold unconditioned air into your house like a natural draft furnace.

If the furnace is sized right, it will have longer run cycles, and eliminate stagnate air problems, weather direct vent or not.
 
More likely then not, the old furnace was over sized.

What your research didn't tell you. Is that your new furnace requires more air flow then the old one did.

Hopefully, the contractor you find to install it for you, will know this, and know what duct corrections you will need to have done. To keep from damaging the new furnace.
 
What we are trying to tell you is that direct vent has basically nothing to do with indoor air quality. Direct vent deals with combustion air and nothing else.
You may have a short cycling issue?
You may need some sort of ERV?
Hard to tell with the information given.
 
Save
If you bought the same sized furnace as the original, then it is oversized.

Your original furnace used natural draft to vent the furnace and was maybe 70% efficient, new furnaces are at least 80% efficient, that is if they use the same chimney as your original. A direct vent is usually vented with PVC and are rated at 90% or better.

Let's do the math, 100,000 btu at 70% AFUE = 70,000 btu output
at 80% = 80,000 btu, at 90% = 90,000 btus. So the same furnace at 90% has an output of 20,000 btus more.

Now to make things worse, when your house was built, it probably was not as tightly built, over the years with new insulation, windows, doors, weather stripping, and lower temperature setting, your house may require much less heat.

In the old days installers did not use Manual J as it required math skills, it was much easier to use a rule of thumb.
My boss from many years ago used 40,000 btus per floor, with the basement loss of 10,000 btus, these figures represented output values. So a 1 story house got 50,000 btus, and a 3 story got 160,000 btus. On many we occasions twined furnaces to achieve these numbers. If the house was as he said scary big, he used 60 btus per square foot as his sizing method.

Nice thing about time, I have changed many of these furnaces, on one occasion I removed two twinned 175,000 btu furnaces and replaced them both with one 125,000 btu 92% furnace. The heating bill on this house when from $1200 a month to $300.
 
Save
Closely related question

Not meaning to hijack the thread, but this does closely relate to the original question:

A family member moved into a brand new house this month with a 90%+ furnace.

When I looked in the furnace room, I noticed only one PVC pipe was hooked up to the furnace (exhaust). There was a spot for the combustion PVC to hook up but it wasn't. Instead there was (what I can assume is) an intake duct that comes down and opens up right beside the furnace.

Isn't it normal to run a second PVC for combustion air? This house doesn't even have a gas hot water tank, its electric. So it didn't seem logical to me.

I guess the answer to this would be the answer for the original poster.

Thanks.
 
Not meaning to hijack the thread, but this does closely relate to the original question:

A family member moved into a brand new house this month with a 90%+ furnace.

When I looked in the furnace room, I noticed only one PVC pipe was hooked up to the furnace (exhaust). There was a spot for the combustion PVC to hook up but it wasn't. Instead there was (what I can assume is) an intake duct that comes down and opens up right beside the furnace.

Isn't it normal to run a second PVC for combustion air? This house doesn't even have a gas hot water tank, its electric. So it didn't seem logical to me.

I guess the answer to this would be the answer for the original poster.

Thanks.

Some manufactures do allow a 2-pipe 90+ gas furnace to be single piped. Usually that involves some sort of intake pipe being installed and open to the basement. This style of installation does of course, eliminate the "sealed combution" feature of the furnace and also requires makeup air for the home, since all combustion air will be taken from inside the home. Our company is in snow country and we NEVER install a 90+ with only one pipe. The biggest advantage, IMO, with 2-pipe is that if the exhaust vent gets buried in snow, so will the intake. That will shut down the furnace and be an inconvenience but that's it. No carbon monoxide issue. Absent that fresh air intake, CO is still a potential problem if the exhaust vent gets obstructed. However, this issue has nothing to do with the original post.
 
Save
Can anyone tell me the benefits or difference between a direct vent furnace setup compared to non-direct vent furnace? With direct vent would this eliminate the stale/stuffy air during the cold winter season? I bought a Goodman GMH95 series and before the installation I am considering is the modification to direct vent since my old furnace does not have this setup.
As some have suggested, an oversized furnace can create hot/cold issues in a home. The hot air comes on during a call for heat and is distributed likety split into the home at some very high BTU/hour rate, shutting down the T-stat in rather short order. A nice 2-stage furnace, properly sized for the home goes a long way toward minimizing any such problem. But I suspect your may have another issue.

The other issue could be dryness in the home. This is a direct result of heating the air in your home. When the air is heated the RELATIVE humidity drops. That is, the air becomes less dense but the amount of moisture in the air is unchanged. Since the air can now hold more moisture compared to when it's at a lower temperture, the amount of moisture actually in the air is relatively less than the air could hold if it were at its saturation point. The solution to this problem is to add a humidifier to the system. Humidifers come in different sizes, just like furances. When sizing a humidifier, the air exchange rate through the home must be taken into consideration. For homes or individuals who need/desire a lot of moisture in the air, I'd recommend a steam humidifier with an automatic flushing cycle. Having a furnace with a variable speed blower motor allows you to run the blower 24/7 at minimal electrical expense and take full advantage of whatever humidifier type you select. :)
 
Save
I was thinking that possibly it was not direct vented for a reason. Possibily to allow moist make-up air to enter the house? We're near the ocean, somewhat damp climate. This would be the "opposite" of the original posters intention.
 
I was thinking that possibly it was not direct vented for a reason. Possibily to allow moist make-up air to enter the house? We're near the ocean, somewhat damp climate. This would be the "opposite" of the original posters intention.
Never heard of any reason like that. We're directly on the ocean as in the North Atlantic and as I stated, we ALWAYS two pipe our systems. The only reason I know of NOT doing the 2-pipe is to save on installation time. Low bidder probably.
 