Dehumidifier electrical wiring

5.2K views 13 replies 9 participants last post by  teddy bear  
#1 ·
Hello all!

Looking for some advice on electrical wiring requirements. I am looking to get a dehumidifier installed and my HVAC contractor quoted me an install for an Aprilaire E100V unit (6.9 amp current draw) but was requesting a separate 20A circuit installed in the attic where it will be installed (3 story house). Currently I have two plugs accessible in the attic and each plug is on its own 15A circuit breaker. One plug is powering the gas furnace (York TM9V100C16MP12CA). The other plug is powering a Rinnai V75i tankless water heater (4 amp current draw).

Is it possible to use either one of these circuit breaker to power the dehumidifier as well? Or do I need to find another circuit or install a separate circuit breaker.

Thanks in advance.
 
#2 ·
No. Why would you think a 15 amp circuit would be acceptable for a 20 amp appliance?
 
Save
#8 ·
But homeowners know everything! The internet says so.
 
Save
#12 ·
If the minimum ampacity is 12A, then a DEDICATED 15A circuit should suffice, but the installation manual may specify a dedicated 20A circuit.

As mentioned above, compressors and fans have inductive loads MANY times higher than running load. Some over 10 times.
Unless you want breakers tripping out whatever else you have on the circuit… I’d get a dedicated circuit installed.
 