Had to work on a RTU today for the one resturaunt we have under contract. Turns out the bottom half of the evap was frozen and circuit 1 suction line all the way to compressor. Thinking the problem was in circuit one I disabled it and ran circuit 2. Immediately after coming on the compressor pulled into a vaccum. I also noticed that several of the feeders immediately frosted over. Each feeder seems to have its own metering device so I assumed that the frosted ones had restrictions. After 2.5 hours of coil defrosting I finally disabled circuit 2, ran circuit one, added about 2 pounds of freon, and left them above freezing for the night. I told them they need to replace the evap coil, am I on the right track here? Thanks for your comments.