Good day!
I came across certain procedure in York Chiller O&M manual (160.54-O2) about "Checking the Refrigerant Charge During Unit Shutdown".
Accordingly, "....the refrigerant charge should always be checked and trimmed when the system is shutdown. The refrigerant level must be checked after the pressure and temperature have equalized between condenser and evaporator. This would be expected to be 4 hours or more after the compressor and water pumps are stopped. THE LEVEL SHOULD BE VISIBLE IN THE SIGHT GLASS...."
However, when i checked our standby Chillers (YK - 2400 TR with refgt charge of 3,042 kgs), the refrigerant level is not visually seen thru the sight glass. Does this means, insufficient charge???? or is the written procedure irrelevant??? The fact that we have added refrigerant from 2,846 kgs to 3,042 kgs, i was expecting the liquid refrigerant level can now be seen through sight-glass of the chiller while they are shutdown.
I have spoken to the local chiller technical guy of JCI. According to him, when the chiller is shutdown, this refrigerant level is insignificant. However, I thought of seeking opinion who has experienced the same concern through this forum to better understand why it was written but not being followed.
I understand that the refrigerant level in the sight glass does not guarantee 100% the correct refrigerant charge/weight. However, it is useful to track the level by monitoring it periodically to identify losses which would result to poor efficiency if not detected.
I came across certain procedure in York Chiller O&M manual (160.54-O2) about "Checking the Refrigerant Charge During Unit Shutdown".
Accordingly, "....the refrigerant charge should always be checked and trimmed when the system is shutdown. The refrigerant level must be checked after the pressure and temperature have equalized between condenser and evaporator. This would be expected to be 4 hours or more after the compressor and water pumps are stopped. THE LEVEL SHOULD BE VISIBLE IN THE SIGHT GLASS...."
However, when i checked our standby Chillers (YK - 2400 TR with refgt charge of 3,042 kgs), the refrigerant level is not visually seen thru the sight glass. Does this means, insufficient charge???? or is the written procedure irrelevant??? The fact that we have added refrigerant from 2,846 kgs to 3,042 kgs, i was expecting the liquid refrigerant level can now be seen through sight-glass of the chiller while they are shutdown.
I have spoken to the local chiller technical guy of JCI. According to him, when the chiller is shutdown, this refrigerant level is insignificant. However, I thought of seeking opinion who has experienced the same concern through this forum to better understand why it was written but not being followed.
I understand that the refrigerant level in the sight glass does not guarantee 100% the correct refrigerant charge/weight. However, it is useful to track the level by monitoring it periodically to identify losses which would result to poor efficiency if not detected.