Hi'' I only whant to know,the formula for cfm,, Example: I have a York Curbpak Air Handling Unit 50hp, 1750rpm 460volt pulleys sizes (motor p 6'') shaft p 10'' how i obtein the cfm thanks
CFM = Velocity x Area
CFM = BTUH / 1.08 x TD
CFM = E x I x 3.14 / 1.08 x TD
just_opinion,OL77,
With such a large unit, formula #1 cannot get the total CFM correctly since the duct will be too large to get good velocity of the air. The answer will be way off
If by a slim chance it has a gigantic electric heater attached to it, than a qualified technician can use the BTU formula to get an approximated CFM
Factory blower curve is you BETTER bet on the total CFM - no formula. How to do this, please call qualified technician.
Call a company out to measure each supplying grills and add them up. Now that is the BEST way.
Good luck
just_opinion,Tnkihr44,
I some what agree with you. (of course there will be a) But,with such large system, it is very difficult to measure the return air velocity in the duct.
As for the duct leakage, if it leaks that bad, then measure CFM is a waste of time until the leaks are repaired. At the 25% leakage, the building will be in such a nagative pressure that the grills and walls are mold-up and it will sucks you in as soon as you open the door.
Let's be specific on the answer to the post. And not be too generic.
I do agree with Marter, that with those formulas we can get in the ball-park figure.
As I stated previously, size and velocity are relative. On that return duct you mention the typical velocity will be somewhere between 500 f.p.m. and 1000 f.p.m. on nearly every size system. Reading 500 f.p.m. is the same if the duct is 1 sq. ft. or 50 sq. ft.(free open area).with such large system, it is very difficult to measure the return air velocity in the duct.
Duct leakage has little to no effect on bldg. pressurization. The difference between exhaust air and make-up air is where bldg. pressures are determined.As for the duct leakage, if it leaks that bad, then measure CFM is a waste of time until the leaks are repaired. At the 25% leakage, the building will be in such a nagative pressure that the grills and walls are mold-up and it will sucks you in as soon as you open the door.
Well, I have tried to be specific. I measure airflow (and water flow) and calculate coil performances (BTU's) for a living. I have all the latest equipment designed specifically for such. Using heat transfer formulas to back into an airflow is the very least accurate method. Hands down.Let's be specific on the answer to the post. And not be too generic.