I've gotten some very helpful information from this forum as I've struggled to decide what system I should get to replace my old, worn out furnace and A/C unit. Now, I hope I can impose upon you to help me with a point of confusion I have about the new system I've had installed.
The new system is a Carrier Infinity with a 58MVC furnace, CNPHP coil, 24ANA7 condenser, and an “Edge” TP-NRH thermostat. Although the system seems to be working well, I'm wondering if a change in one of the installation options might make it work even better. The option in question is shown below just as I copied it from the installation manual:
Option 32 — Furnace Heat Staging Control (available only when the
Thermidistat Control is configured to operate AC or A2 equipment).
1 — Thermidistat Control controls W1 output only and furnace controls the turn
on and turn off of higher stages of heat.
2 — Thermidistat Control will control the W1 and O/W2/B outputs.
Default is 1.
The thermostat shows this option to be set at “1”, the default. As I understand it, this means that the furnace will stage itself according to its “memory” of how long it took to get to the set-point during its prior cycle. If so, this may explain why the furnace is so casual about raising the temperature when I increase the set-point in the morning. (This isn't a big deal right now because it isn't very cold, but I wonder if it might be in mid-winter.)
The thermostat spec. shows that it is capable of controlling a 3-stage furnace, but I have no idea if the signals shown in setting “2” actually do that or not. If they do, I wonder if “2” might be a better setting because the thermostat at least knows the difference between set-point and room temperature, and might, therefore, stage a bit more aggressively when necessary.
Naturally I'll speak to my installer before I change anything, but I'd greatly appreciate any comments you folks might have before I do.
The new system is a Carrier Infinity with a 58MVC furnace, CNPHP coil, 24ANA7 condenser, and an “Edge” TP-NRH thermostat. Although the system seems to be working well, I'm wondering if a change in one of the installation options might make it work even better. The option in question is shown below just as I copied it from the installation manual:
Option 32 — Furnace Heat Staging Control (available only when the
Thermidistat Control is configured to operate AC or A2 equipment).
1 — Thermidistat Control controls W1 output only and furnace controls the turn
on and turn off of higher stages of heat.
2 — Thermidistat Control will control the W1 and O/W2/B outputs.
Default is 1.
The thermostat shows this option to be set at “1”, the default. As I understand it, this means that the furnace will stage itself according to its “memory” of how long it took to get to the set-point during its prior cycle. If so, this may explain why the furnace is so casual about raising the temperature when I increase the set-point in the morning. (This isn't a big deal right now because it isn't very cold, but I wonder if it might be in mid-winter.)
The thermostat spec. shows that it is capable of controlling a 3-stage furnace, but I have no idea if the signals shown in setting “2” actually do that or not. If they do, I wonder if “2” might be a better setting because the thermostat at least knows the difference between set-point and room temperature, and might, therefore, stage a bit more aggressively when necessary.
Naturally I'll speak to my installer before I change anything, but I'd greatly appreciate any comments you folks might have before I do.