Hi Guys been a while since i posted. After some suggestions please.
Working on a 30 hxc which runs high discharge pressure on circuit A causing it to limit.
Circuit B running ok so would think water flows etc good.
Circuit A discharge pressur 1200kpa, discharge temp 65c. discharge superheat 16 c.
Suction pressure 285kpa . checked exv and seems to sit around 34% open.
it limits and backs off to 70% capacity .
Condenser water in 26c out 32c
circuit b runs about 950kpa discharge at 100% capacity, suction at 285kpa.discharge superheat 10c and exv sits around 32% open.
Any ideas would be greatly appreciated.
Cheers