Actuated exhaust dampers. The AHU is not set up as such, it has a heat recover wheel so as air enters: OA damper, summer filters, pre heat coil, winter filters, bag filters, supply fan, heating coil, cooling coil, supply ductwork. Then air heading back to the return goes: return damper, return filters, return fan, heat wheel, exhaust damper. The bag filters are plugged, starving the supply fan and causing it to ramp up.
Duct static pressure sensor always sensed too low (.3" or less no matter what). I verified with a manometer on the pneumatic tubing at the sensor that I was reading .6", and verified that the sensor was reading incorrectly. The new is a 0-5" wc, 4-20 mA differential sensor and is a different manufacturer but the same thing. Used formula from new sensors literature to verify proper mA reading compared to the static pressure. The math worked out perfectly. As previously stated though, BMS varies supply fan speed depending on duct static pressure (sensor I changed). Moving more air then it thinks though is possible, it also uses the exact same differential pressure sensor hooked up to an airflow station at the inlet of the supply fan to determine the l/s (metric cfm). I see what you mean, and agree, this reading could be off and throwing off the BMS return calculation. That brings up another good point, I could do use that same math formula to determine that the fan cfm sensor is reading properly (unless the flow station itself has a problem, or the pneumatic tubing).
As ckartson said, I believe he's correct, I think honestly it's always that high because of again, the exact same sensor, reading improper flow through the air valves that feed other air handlers. 5 air valves at the end of the duct work are all %100 open all the time, most likely the culprit.
It's true that not all exhaust fans are working. 1 is used in a garage area that only comes on when the CO is high (this is at an airport, where the baggage carts drive in so the employees can rough house your breakable items).The computer still assumes it's always on in it's calculation, (Mind you, large doors open frequently in this area)Unless the BMS smart enough to know when the fans are off, but then I should see that return fan vary it's if I turn that exhaust fan on, pretty sure it won't but I'll try it tomorrow to verify.
I spent half a day lighting a lighter and watching where the flame blew through different doors... haha. I got a lot of strange looks that day, that's for sure.
The only other noteworthy thing I can think of to mention, is that I know this duct was pulling air in only a few weeks before I posted this, I actually used the combustion air duct's winter air to cool something down. This was still sucking air, even after I changed the static sensor. The one thing that did change, is that we have the heat reclaim wheel tied so it won't spin right now, because the reclaim motor brushes were f'd. The reclaim wheel normally free wheels and spins in the proper direction when not tied down. I can't imagine this could be causing any balance issues though?
Aye, sorry for the long winded posts, it's almost impossible to convey an adequate amount of information.