thanks guys! it has to look good as its in my kitchen! plus im very OCD w/ all my work
I knew this would happen , now I have to break system down, Im so lazy w my typing haha]
I have purposely mixed it up as much as possible with sole purpose of gaining modbus experience and especially bacnet integration
1) top 5 grey devices are Innotech maxim range ddc controllers, circa 2005 ,w 1 subsystem gateway allowing access TCP to network and service laptop, these speak on their own rs485 net comms and global comms, (for bacnet on maxim requires seperate gateway)
2) the blue device is Innotech`s new Omni controller! (which acts as my "head end " on this panel.) which hardware will be released by the end of 2016 and I have been lucky enough to have access to new controller early along with beta release software.
Native bacnet device IP/mstp, 2x ethernet connections with choice of using as ip switch mode or simply device ip in/out. all points are univ I/O!(14-20-or40) 3 x univ comms ports, this allows for backwards compatibility to maxim range with "global" block data, allowing you to monitor maxims onto , omni webserver which is like a work station in itself!can monitor up to 10 controllers. Ports can be eg 1) net comms 2) global comms 3) mstp , or eg 3 x mstp seperate connections to break up mstp.
http://innotech.com.au/DownloadFiles/Documents/innotech_omni_ds.pdf
3) middle right is contemporary controls BASremote sedona controller bacnet ip to modbus which will talk solely to altivar drive (top left, which is a small single phase to 3 phase 1/4 hp) , target is to bring the modbus point out of device to bacnet ip and rocknroll through sedona to omni, Have just completed the mapping registers and all talking there
4) fieldserver protonode ( thank you ORION!!) grey center has been unlocked w some support from its factory boiler manuf default so now i have a very powerful gateway, Its target is 1 x modbus rtu stopbit 2 to carel Ir33 univ ctrlr ,(white center)
1 x modbus rtu stopbit 1 , to 1x syxthsense modbus room controller (bottom left/top) and outwards bacnet/IP to omni port in switch mode
5) Contemporary Controls BASrouter bacnet IP to mstp (center black) will talk to 1 x sysxthsense mstp room controller( bottom left corner) , yes omni has mstp output , But as said I wanted to mix it up here.
6) finally all ethernet ports travel thru Contemporary Controls BAS switch outwards to laptop.
I think they have a winner here w Omni , solid hardware and if you read the data sheet and see how much you get built in for the price competitiveness its amazing , The Aussies were here in UK and Ireland for 2 weeks doing partner Omni technical training I was lucky to be included, and were Just in states 4 weeks , I think the plan is to start attacking consultants hard and heavy worldwide USA, European continent etc, I am happy I found and chose this manuf to work with excellent support without corporate feel, 100% designed and manufactured in Australia , not 1 chinese part. they are running well behind on release , but w 2million$plus in research you can surely see they want it to be perfect!
cheers, stan