jvarney

· Registered
Joined
·
10 Posts
Discussion starter · #1 ·
I have a new aprilaire 600 installed humidifier. on a Trane Heat pump humidifier. I think I have a bad humdifier control "Stat".

The humdifier will not flow water in test mode,auto or manual mode.
24v power is getting to the control "stat" "R\C" but no power is coming out "The two H leads".

This this mean the stat is bad or could be something else. I am checking for power at the stat leads. Also should the stat "R\C" leads have power only when the fan blower is running?
 
Why would you troubleshoot someone elses work? Did you install this yourself?
Tisk Tisk Tisk

We can't give diy advice.

Is the water tap ON?
 
Save
Discussion starter · #7 ·
Yes I have already verified that the water is on and flowing if I remove the tube on..... The wiring looks very sample and would just like to know if I have power coming in should it have power coming out of the stat to the humidifier. It could be a very few things wrong.....
 
Yes I have already verified that the water is on and flowing if I remove the tube on..... The wiring looks very sample and would just like to know if I have power coming in should it have power coming out of the stat to the humidifier. It could be a very few things wrong.....
It is apparently over your head, call the installer.
 
Discussion starter · #19 ·
Thanks Hvac_Superman.... That is what I thought since that is only way the humidifier it will get power.... the other problem it has power all the time with fan or not, they have it power ran wrong and could have shorted out the stat....
 