OK!
First, manual for the drive is#ACS-400.
Second, went to job today after getting approval from customer to do repairs.
Installed a pilot relay for fresh air damper motor with manual pot to adjust quantity.Installed another pilot relay to oprn return air damper before start up of fan.
During this time power was off and I checked motor for shorts and grounds and found none. Motor resistance accross windings was 7 Ohms. Checked all electrical connections and contactors (both accross line and VSD contactor, like new).
Powered up unit and Fault #4 SHORT CIRCUIT was gone and drive showed no falts or alarms. I left the drive in OFF mode and put unit selector switch to " BYPASS" and what do you think happened????????
NO AIR FLOW alarm, motor on bypass was in reversed rotation!!!! Sooooooooooooo I reversed leads at fan fuse block (Assuming drive would still operate, Stupid me!)and I started up fan in bypass again and fan came on in the proper rotation and running a little below rated amperage.
Turned unit to off mode and put selector switch to Inverter mode. Turned unit on and when VSD engauged, the motor started to vibrate as it came up in frquency?????? and was trying to go backwards????
So I said now what??? Well since I reversed at fuse block let met change a phases at Inverter contactor. Now I restarted unit and motor started ramping up in the right direction but there is alot of vibration as it ramps up???
Drive will bring it up but there is defintly something not right?
This vibration is not bearings, belts,alignment,etc.. Its something to do when the drive is ramping up, its like the motor is trying to go both ways, like its STUDDERING.
Left unit in bypass for weekend. The manual is of no use as far as trouble shooting and you have to dial a mess of numbers for ABB info. They dont even respond on their web site! Any suggestions or numbers would be appreciated.
ABB TYPE # AGH401601132
CODE # 64078917
SER# 204010077
Hope I'm using the right manual, customer said it came with unit and McQuay did start-up.