The fan motor pulls a max of 16 amps when ran at 60hz. Is there something inside the vfd that could be giving this false trouble?
Sent from the dust in front of you!
Sent from the dust in front of you!
Need more info. Did you program motor info in start menu(para. 99)on vfd? Ramp up time if too short will cause over amping ,30 seconds is default. Program max amps in parameter 21. Is it the correct vfd for your application? VFD should be sized by motor amps and not by motor horse power.
If drive sized correctly, most of the time I find ramp time to short, Just like Ken said. Also,ABB support is good though