Hi guys! My name is Sunny and I’m new to this site and I just want to say first off that I truly appreciate any response and feedback that I receive! I’m a Maintenance Technician at a apartment community where I live and right now I have an issue where a resident’s 5 amp fuse on the board in their air handler continues to blow every few hours. It doesn’t blow immediately and their heat will work for a few hours but it will eventually blow again. Any advice on diagnosing this issue will be greatly appreciated! Thanks a lot!
 
If that's a heat pump, it sounds like a short in either the defrost or maybe second stage heat. Might try manually tripping a defrost cycle and see what it gives you. Hopefully it would at least allow you to replicate the issue to trace it
 
You need a good amp meter around the fused line and then start cycling all the components, if nothing shows a high amp draw, start looking at all the control wiring for chafing or bare spots.
 
Save
You have a intermittent short. As has been said it may be from water getting on a wire during defrost. It could be from a vibration against metal, etc. Get out your shovel cause the only way to find this is to "dig" into it. If it were constant it would be fairly easy to track down. Being intermittent you will almost have to live with it till it happens. As said you may be able to run the system in all it's modes but trying to shorten the time frame may not let all the components of the short come together. You may be able to get creative with smaller fuses to isolate the problem but can't go into particulars on an open forum.
 
Save
Instead of constantly blowing fuses, get a product called short pro, you can find it on amazon, if you want to see it in use, look up Dirty maintenance show on you tube, done by Lex, who is a maintenance man himself, he recently did a video on a short in an indoor unit. He might be able to give you more advice than we can share on this open site!!!


Sent from my iPad using Tapatalk
 
Save
Sounds like a bare wire for reversing valve rubbing and causing the short when goes into defrost. Switch to Ac and see if blows immediately if not then keep digging.


Sent from my iPhone using Tapatalk
 
Check LPC & HPC. I ran into a couple of the screw on with the plastic cover on the switch. The plastic was cracked so water could get in which could cause an intermittent short.
 
Save
I would put a little 5 amp "lil popper" breaker on- (that is brand)- to avoid wasting fuses. (in addition to what everyone else has said). When I have had this problem- I found wiring issues from previous tech---check each wire with schematics- it just takes a few minutes, but then you know where you stand. You know everything is wired properly- and then you can start inspecting wires and circuits for shorts like the others have said. In the meantime you are not wasting fuses.
 