Lennox LGA/LHA180 package unit
Ambient: 85°F
Condensing temp: 122°F
SC 1: 34°F
SC 2: 18°
SC 3: 25°
Evap temp: 42°F TXV metering
SH 1: 20°
SH 2: 38°
SH 3: 20°
Return: 81°
Supply: 55°
Thermostat set for 76° but manager says it never hits that.
Filters clean, belt tension good, bad economizer so outdoor air is always mixed in with the return. It's a kitchen unit for Mcdonalds so there is a lot of heat to absorb.
Any ideas on why I'm getting drastically different SH and SC but all pressures are exactly the same?