I recently left a startup troubleshoot. Here are some details:
Mitsubishi PUMY-060 outdoor unit connected to several Mitsubishi indoor units. The original call was a "No AC" call. Our tech showed up, found the LED display in the PUMY showing error code 4100 - "Compressor current interruption (Locked compressor)." Our tech then diagnosed a bad compressor via "a bad winding" and a bad power board (not sure how power board was determined).
We replaced both components, only to find the same problem present itself at startup - compressor drawing locked rotor amps, no start. The tech doing that startup checked the compressor and found it grounded. Thinking it was a bad compressor from the factory, that tech ordered another compressor.
The second replacement compressor was then installed and also didn't start. Again, error code 4100. That tech began troubleshooting, and determined the power board was bad, leaving the following notes: "Checked compressor and wire connections from circuit boards and voltages. Found compressor windings, wire connections, and voltages are good except inverter output. Inverter output to compressor is bad due to voltage cutout during demand."
I went to replace the power board. Compressor still failed to start. I found the compressor grounded and measured amp draw of 25A during the brief period it did try to start. LRA for this unit was listed at 21A, RLA at 19A. At one point the compressor even shook around some while trying to start. Error code 4100 arrived again. I wasn't able to find any misconnected wires. I checked the compressor terminal with a megger and found the windings grounded. I did not order another replacement compressor, need to return to troubleshoot.
Where would you look to find the problem at this point?