I have an eng a mua unit with a fireye control. This unit has been giving me nothing buit problems. When I first started on this unit I found a bad burner ground, cleaned ground to solve that problem. also found burning poorly, cleaned burner, burner very well, good blue flame. Have had fire eye trip out several times with just the alarm light on. Yesterday however it did lock out with the op ctrl and alarm light on. This is telling me line frequency noise alarm, any ideas. Also it has been tripping out for about two months now intermitantly. I have checked static pressure drop across burnes at 5.7 to 6. My low pressure switch is set at .1 and high presssure air flow switch is at 1.5. Checked my gas pressure at it is set properly. My da sensor hooked to my maxitrol amp all seems to be working fine. I also have another unit of the same type with out a vfd in it. I switched the fireyes around thinking it was in that burner control, still the bad one trips out and other one keeps running. Any ideas would be great, I can't even think of any thing else to try. And if any info on line frequency lock out would be great. Thank you for your help